Hello,
I have two questions that I cant seem to figure out. Could someone point me in the right direction?
A 240v single phase circuit has a connected load of 10A. The total conductor length is 400' and the resistance is 1.75 ohms per 1000'. What is the net computed loss of this circuit in watts?
a) 70
b) 123
c) 175
d) 350
correct answer is a) 70.
Where do i begin if I dont have a wire size? I tried this for about a half hour and major brain cramp. any help would be appreciated. what am i missing/overlooking?
The other question is motor efficiency.
A 120v, 1/2HP, 80% efficient ventilation fans is replace with a new 120v, 1/2HP, 90% efficient ventilation fan. The new fan will draw what percent less current?
a) 10
b) 11
c) 20
d) 21
The answer is 11%. I came up with 7.84a on 80% and 8.82a on 90%. Why not 10%. the difference is .98 amps. the only way i got to 11% is 8.82x.11=.9702. does anyone know the proper method for this situation?
any help would be appreciated. just looking for a bump in the right direction on how to figure these out. thanks
a) 70
b) 123
c) 175
d) 350
a) 10
b) 11
c) 20
d) 21