- Location
- Illinois
- Occupation
- retired electrician
There is a 2000kva transformer with 3-phase 480 volt solidly grounded secondary. It is connected to metal clad switchgear with 3000 amp rated bus duct. There are a number of 600 amp breakers that are feeding MCCs with parallel 350 kcmil copper. The available fault current at the MCCs is between 32 to 39kA. The MCCs are rated for 22kA. Would it be feasible to install a reactor between the transformer and the metal clad switchgear to reduce the available fault current at the MCCs? I looked around on the net a bit, but did not find much in the way of information on using a reactor for this purpose. This installation has been in place since the early 70's and the problem just came to light as a result of a short circuit study that was being done for the purpose of specifying arc-flash PPE.
Note, this is just for my information, the method of correcting this problem will be specified by a design engineer. There are a number of possible solutions being considered including MCC replacement and reactors for each MCC and maybe others.