bongo44

New member
It's my understanding that you're not supposed to install VFD's below overhead water pipes. Plausible location options are limited in the space I'm looking to put some VFDs - is there some sort of shield or cover for the drives that can be used so that it's acceptable to put them under pipes?
 

Besoeker

Senior Member
Location
UK
Use an enclosure with cabinet coolers
That's what I would do.
But, unless they are (expensive) indirect coolers, they would negate the NEMA 4 classification.
That was my point. Puting drives or any power dissipating kit in a sealed box is generally best avoided in my opinion. I have seen it end in tears more than once.
For the problem in the OP, a drip-proof canopy would be a simpler and cheaper option.
 