Step up transformer 208v to 400v 3 phase

Status
Not open for further replies.

amge

Member
I have a job to wire up a step up transformer 208v to 400v for a utilized peice of equipment (spray booth). The drawings indicate that I need a 30 amp 3 phase, 4 wire circuit with disconnect switch and thats all. The customer will supply the transformer. My question is do I need over current protection on the secondary side or will the 30 amp 3 phase breaker be sufficent for the primary and secondary of the transformer.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
depends on the size of the transformer and wiring length.
You need to look at 450.3 amnd 240.21(C)...lots of varibles..
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If this is a delta/delta transformer, then a properly sized primary OCPD can be used to protect the secondary conductors. 240.21(C)(1). If it is any other type of transformer one of the other rules in 240.21(C) will apply.
 