Residential 120/240v Generator Grounding Conductor Sizing

Status
Not open for further replies.

st1976

Member
Location
CT
Hello all,

I am installing a residential 120/240v 1ph generator (not portable). The automatic transfer swith does not switch the grounded conductor.

The unit is a 10KW.

I am sizing the grounded conducter to match the phase conductors, #8 copper.

Is the grounding conductor sized by 250.122? #10 copper based on the 40A cb in the transfer switch.

Thanks
 

raider1

Senior Member
Staff member
Location
Logan, Utah
The EGC for the generator should be sized based on the overcurrent device protecting the generator.

What size breaker is installed in the generator?

Chris
 

st1976

Member
Location
CT
The EGC for the generator should be sized based on the overcurrent device protecting the generator.

What size breaker is installed in the generator?

Chris

Chris... thanks for the response.

The 40A breaker in the transfer swith is protecting the generator. I don't believe there is another breaker at the generator itself. I'll have to double check.
 