I'm installing a baggage handling system at Miami International Airport. The conveyor is approximatley 24" from the concrete wall. I have a 480v 3.5 HP motor disc. switch along with 120v control boxes on this side of the wall. The airport inspector is telling me that there must be 36" clearance. I could probably agree on the switch. but not on the controls. What say you?
 

pfalcon

Senior Member
Location
Indiana
110.26(A) appears to be the reference you need to study.
The switch is actually condition 2 (backed by a concrete wall) at 480VAC and therefore 3'6" not 3'.

If what you refer to as "control boxes" are nothing more than pass-thru or terminations then they might bypass 110.26(A). If they contain fuses, relays, or other control components then 3'.
 