tetay56@yahoo.com
Member
I'm installing a baggage handling system at Miami International Airport. The conveyor is approximatley 24" from the concrete wall. I have a 480v 3.5 HP motor disc. switch along with 120v control boxes on this side of the wall. The airport inspector is telling me that there must be 36" clearance. I could probably agree on the switch. but not on the controls. What say you?