hardworkingstiff
Senior Member
- Location
- Wilmington, NC
Saw a 3" PVC conduit install that had more than 360 degrees in bends between the panel and a juction box. Conductors to be pulled are (3) 500kcmil and (1) #3 THWN. There is a 3" C condulet installed in the raceway so that there is less than 360 degrees of bend between pull points. I didn't measure it, but that C couldn't have been much more that 14" long. I didn't take the cover off, but I'd wager the C is not stamped for the conductors to be pulled.
So here's my question. Shouldn't that C meet the requirements of 314.28(A)(1) and should be 24" long?