do you have to ground a metal box, if you pull it in romex?
do you have to ground a metal box, if you pull it in romex?
how does that clip work, dont you need a green wire tied to it?
Of course... That's why they make them silly green screws... Oh - contrary to popular belief - you have to ground the device you put in it too...
my reply was to post number two. Please show me a code article that says I have to ground the device along with the box. I'd like to see it.
do you have to ground a metal box, if you pull it in romex?
Don't have my book in front of me but I'd say if the romex was just passing through the box without being stripped and terminated to a device, the box would not have to be bonded.
Don't have my book in front of me but I'd say if the romex was just passing through the box without being stripped and terminated to a device, the box would not have to be bonded.
Not so, 250.4, and 250.86-ish off the top of my head. The box must be bonded, even if no conductors are spliced within the box. Also see 250.148.
To paraphrase Gary Seinfeld, "Why have a box?"Don't have my book in front of me but I'd say if the romex was just passing through the box without being stripped and terminated to a device, the box would not have to be bonded.