JohnJ0906

Senior Member
Location
Baltimore, MD
300.4(E) is not referenced in Article 725 or 760 so it does not apply.


90.3 Code arrangement
".......Chapters 5,6,and 7 aplly to special occupancies, special equipment, or other special conditions. These latter chapters supplement or modify the general rules. Chapters 1 through 4 apply except as amended by Chapters 5, 6, and 7 for the particular conditions. ....."

If 300.4(E) is not referenced, then it fully applies.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
90.3 Code arrangement
".......Chapters 5,6,and 7 aplly to special occupancies, special equipment, or other special conditions. These latter chapters supplement or modify the general rules. Chapters 1 through 4 apply except as amended by Chapters 5, 6, and 7 for the particular conditions. ....."

If 300.4(E) is not referenced, then it fully applies.
John,
Take a look at 725.3 or 760.3.
725.3 Other Articles.
Circuits and equipment shall comply with the articles or sections listed in 725.3(A) through (G). Only those sections of Article 300 referenced in this article shall apply to Class 1, Class 2, and Class 3 circuits.
760.3 Other Articles.
Circuits and equipment shall comply with 760.3(A) through (G). Only those sections of Article 300 referenced in this article shall apply to fire alarm systems.
 