thanks for the links. The UL website can be a little frustrating to get what you're looking for though. At least for me. All I can assume is that the bonding takes place at the locknut and threads being electrically continous through to the enclosure. Although I wish it said that specifically somewhere. If it does please let me know. I work with a journeyman that insists I put bond bushings on any flex or sealtite regardless of the circumstances.
Keep in mind that FMC and LFMC ( flex and sealtight ) can only be used for grounding on
circuits of 20 amps or less, above that it needs a wire type EGC, per 250.118.
So, on circuits over 20 amps, using bond bushings on FMC or LFMC is a complete waste of
your time and money. Would the J-Man have you put bond bushings on PVC fittings ? I
don't think so, it is not part of the bonding path and neither is FMC or LFMC over 20 amps.