GG
- Ft.Worth, T.X.
Im seeing this alot where an installer taps into the air handler circuit with a 10/2 to send power to the outdoor condenser on an HVAC install. Other than being an NEC violation are there any real hazards with doing this? Im trying to think of some and none come to mind. I need more ammo to go to the owners with other than "well the NEC says you cant do that". I tell them about the NEC and what it will cost to correct it only to get hit with "well than why has it been working for 10 years that way if its wrong"?
The air handler comes with a 2 pole 60 and a 2 pole 30 amp breker installed. The unit has 3-5 kw heat strips. Normally I will run a 6/2 romex and a 10/2 romex to feed the 2 breakers. What HVAC companies will sometimes do is what you see in my pics. They run a #4 wire and land it on the 2 pole 60 and then use 2 #10 jumper wires and go breaker to breaker. I know the breakers are not listed to have 2 wires under each termianl as they are doing with the 2 pole 60. If they used a split bolt and tapped the #4 wire and then ran a wire to each of the 2 pole breakers Im pretty sure the NEC tap rules forbid this as well.The outside condenser must be protected at it's name plate maximum breaker size. I am not sure about the taps.
Are they an internal part of the unit?
Yes, unfortunatley it is. There is 50' running through the attic thats not in conduit. For some reason they shoved a PVC 90 into the air handler and sleaved the wires in that so they obviously knew the wires should have been in some type of conduit.Is that just THHN with no conduit feeding the unit?
I see absolutely nothing in that picture that complies with the NEC.
This is a text-book example of how not to do this work. Unbelievable. :roll:
Im sure they were the "lowest bidder". Around here thats all that seems to matter, the price. Im sure the owners never looked at the final install and just went by price. Its 20' back in an unlighted attic so Im sure other than the original installers Im the only one to have seen it. Now I get to try and explain to the owner why something that has worked for 10 years now needs to be cleaned up.I see absolutely nothing in that picture that complies with the NEC.
It was a no heat call. The condenser units contactor was locked in the closed position and this caused the evaporator coil to ice over. I melted the ice on the coil and got the heat working. I told the owner that they need to install the wire properly.What brought you into the attic? Was it service/trouble shooting, or did you stumble upon this atrocity while working on another project?
Im also an HVAC tech. I gave the owner the option to fix it and they declined. I would bet an HVAC company is the one who installed the circuits as part of their "package deal".If they called the HVAC Tech. would they have left it. ? !
Some of the worst service changes I've seen were part of an HVAC install "package."I would bet an HVAC company is the one who installed the circuits as part of their "package deal".