Sizing OCPD and Wire for HWH

Status
Not open for further replies.

tyha

Senior Member
Location
central nc
we have a water heater with upper and lower elements that run do not run simultaneously. The unit is marked 3PH 4500W upper and 4500W lower. Doing the math it comes out to be about 12 1/2 or so amps which would be 3p 20A CB with #12 Thhn. Why am I thinking that is wrong and it needs to be #10. maybe because Im thinking of a single phase unit. Am I missing something or is it right?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
From waht you state, all is correct.

I must say it would be a first as I have never seen a 3 phase 4500 watt water heater nor have I seen a 4500 watt 208 unit. (most 4500 units I have seen are @240)
I hope you have actually seen the nameplate and not relying on hearsay.
 

tyha

Senior Member
Location
central nc
nope. this is exactly how it is stated. upper 4500W lower 4500W total 4500W. the plumber marked the correct model and it states inside the wiring diagram that the upper and lower do not run simultaniously and that it is 3ph and there is nothing that states min ckt or max ocpd
 

hardworkingstiff

Senior Member
Location
Wilmington, NC
nope. this is exactly how it is stated. upper 4500W lower 4500W total 4500W. the plumber marked the correct model and it states inside the wiring diagram that the upper and lower do not run simultaniously and that it is 3ph and there is nothing that states min ckt or max ocpd

How many elements did the wiring diagram show conneted at the to and then connected at the bottom? It should show 3 elements.
 

rt66electric

Senior Member
Location
Oklahoma
flip-flop either/or

flip-flop either/or

I hate to admit it but a @#$% PLUMBER had to explain it to me...
It has a upper and a lower element of the same wattage. There is also a small temp controller on the unit that ... Heats the top element first to desired temp them flip/flops to heat the lower element. the process is more efficient and has a faster recovery time, for longer showers.
 

hardworkingstiff

Senior Member
Location
Wilmington, NC
I hate to admit it but a @#$% PLUMBER had to explain it to me...
It has a upper and a lower element of the same wattage. There is also a small temp controller on the unit that ... Heats the top element first to desired temp them flip/flops to heat the lower element. the process is more efficient and has a faster recovery time, for longer showers.

Just one upper element? How would you hook up 3 wires to one element?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
208 x 1.73 = 360

4500/360 = 12.5

the unit states 4500W total

If this were a test question you left one part out:

12.5amps * 125% = 15.625 would be your minimum circuit ampacity since a storage type HWH is considered a continuous load.
 

paul

Senior Member
Location
Snohomish, WA
These assemblies are usually comprised of three elements, but only one unit. They have three screw terminals that the wires connect to.
 

joebell

Senior Member
Location
New Hampshire
would 422.13 apply to this ,not that it would make a difference in the size of the conductors or OCPD, but just in terms of the calculation?
 
Last edited:

tyha

Senior Member
Location
central nc
it has 3 wires sticking out in a junction box that we connect to. just 3 phase wires and ground and thats it. the wire diagram shows 2 phases going through a coil of some sort and 1 phase going directly from where we hook it up to a timer inside.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
First, the "4500w upper/4500w lower/4500w total" rating is typical for water heaters. Once the upper element is satisfied, it switches to the lower, which switches off when it's satisfied. The lower element gets most use.

Second, I have seen water heaters with diagrams for 1ph or 3ph use. They're wired with two of the three wires connected together for 1ph, and like an open Delta on 3ph, with one conductor shared by both elements.

And, naturally, for a given power level, the current will be lower when the designed voltage rating is higher, because elements of different resistances are used. Having 3ph also lowers line current, and the two advantages add.
 