091203-0844 EST
An EGC equal in size or larger than the phase conductors is a good idea from a safety point of view. But if a CNC is noisy this may not solve the problem. It might take 0000 copper or larger, and then it might still be marginal or not solve the problem.
A few of years ago I had a customer with two similar CNCs side by side, 2 ft between them. Both machines were the same manufacturer and model, but 2 years different in age. Both were wired in a similar fashion from an overhead bus. About 30 ft of wire from the bus to machine and there was an EGC from the bus to each machine. Additionally there was a supplemental ground rod at each machine.
RS232 communication was satisfactory to the older of the two machines. It was impossible to communicate to the newer machine in either direction when its servos were on. Thus, DNC (drip feed) was impossible. The machine vendor proved that there was "nothing wrong" with the machine because he could communicate successfully with the machine from his laptop. Note, he had no common connection to his computer from anywhere except thru the RS232 cable to the CNC, thus no noise on the ground path. The CNC people blamed the problem on the supplier of the computer RS232 equipment.
The CNC was the problem because it was the source of the noise.
The solution to this problem was our RS232 isolator system.
What was the difference between the two CNCs. The older one had DC servos, and the newer one vector drive or brushless servos. Therefore, different servo drivers.
,