Can you have multiple voltages such as single phase 208 and 120 in the same conduit that come from the same panel
Sure u can. keep in mind the derating factor starting from 4 current car. conductors:Can you have multiple voltages such as single phase 208 and 120 in the same conduit that come from the same panel
What about 300.3(C)(1) 600 Volts, Normal, or Less.
Says as long as the insulation is rated to the highest voltage you can mix any voltage under 600 volts, AC or DC
But in NYC voltages over 250v can not . 300.3(C)(1) Ex. No. 2
What about 300.3(C)(1) 600 Volts, Normal, or Less.
Says as long as the insulation is rated to the highest voltage you can mix any voltage under 600 volts, AC or DC
But in NYC voltages over 250v can not . 300.3(C)(1) Ex. No. 2
[FONT=TimesNewRoman,BoldItalic][FONT=TimesNewRoman,BoldItalic]ARTICLE 300[/FONT]
[FONT=TimesNewRoman,BoldItalic]Wiring Methods[/FONT]
[FONT=TimesNewRoman,BoldItalic]SECTION 300.3[/FONT]
[/FONT][FONT=TimesNewRoman,Italic][FONT=TimesNewRoman,Italic]Subsection 300.3(C)(1) - Add a new Exception No. 2 to read as follows:[/FONT][/FONT]
[FONT=TimesNewRoman,Italic][FONT=TimesNewRoman,Italic]Exception No. 2: Barriers shall be provided to isolate conductors energized from[/FONT][/FONT][FONT=TimesNewRoman,Italic]
[FONT=TimesNewRoman,Italic]different sources when system voltage exceeds 250 volts nominal and conductors are[/FONT]
[FONT=TimesNewRoman,Italic]protected by first or second level overcurrent protective devices. Sources include service [FONT=TimesNewRoman,Italic]
[FONT=TimesNewRoman,Italic]entrance points, secondaries of different transformers, generators and UPS systems.[/FONT]
[/FONT][/FONT][/FONT]
Art 725 shoots a hole in assuming any mix is allowable if the insulation rating is high enough.
Hard enought to figure out what they wrote or accepted - never mind what they think....Being a installer not a writer, I can only assume that the powers that be, do not want 110/208v in the same conduit as 277/480v:-?