Hi all,
I'm trying to do a solar PV proposal for a large warehouse in NJ. Code says that the maximum allowable current on a busbar can't exceed the ratings of the OCPDs protecting that busbar. The main switchgear is rated for 1200A, but the service has no OCPD at all (or rather, it probably has one, but it's on the utility side, and nobody knows what its rating is). I'd like to install a PV system which will backfeed through a 750A breaker.. my question is, how do I figure out whether I can do that or not? Do I need to call up the utility and find out what their OCPD is rated for? Or does it fall back to the total allowable loads on the switchgear (which consist of a 700A subpanel breaker, and an 800A subpanel breaker)? Or am I basically home free to land anything up to 1200A? Thanks for any advice,
Bret
I'm trying to do a solar PV proposal for a large warehouse in NJ. Code says that the maximum allowable current on a busbar can't exceed the ratings of the OCPDs protecting that busbar. The main switchgear is rated for 1200A, but the service has no OCPD at all (or rather, it probably has one, but it's on the utility side, and nobody knows what its rating is). I'd like to install a PV system which will backfeed through a 750A breaker.. my question is, how do I figure out whether I can do that or not? Do I need to call up the utility and find out what their OCPD is rated for? Or does it fall back to the total allowable loads on the switchgear (which consist of a 700A subpanel breaker, and an 800A subpanel breaker)? Or am I basically home free to land anything up to 1200A? Thanks for any advice,