If I have a single panel that has 24 circuits in it. It is rated for 70A with
a 70A circuit breaker. The incoming line is 480 and the secondary is
240.
Would the transformer rating be 70(240)(1.73)/1.25(1000) = 23.25KVA?
Where 240 is the secondary voltage?
So I need at least a 23.25KVA transformer?
Is the above correct? If not, what am I doing wrong?
If this is correct and I have 480VAC going to the primary of that
transformer thur a disconnect switch. How do I find the size of
the disconnect switch or circuit breaker?
How to a calculate the wire sizes going thru the disc connect switch
to the transform then the secondary wires to the panel?
Thank you,
Thank you,