Okay, I'm not an electrician or electrical contractor, so I never ever post here - lost my log-in info, actually. But this thread was obviously started in response to
this thread at Terry Love's... so... here I am, cross-posting my response. I'm guessing our odds of having a code-guru settle the question, is a lot higher over here.
I think you've completely misunderstood the exception.
A reference to 300.15 (C), 334.15 (B), and so on, would make it less confusing, I suppose... or you can just read what's written, without trying to "read in" what isn't there:
Exception: Short sections of raceways used to contain conductors or cable assemblies for protection from physical damage shall not be required to be installed complete between outlet, junction, or splicing points.
It's not saying anything about the sequence. Nothing about assembly before, or after, wire-pulling.
All it's saying, is that when you're using a short run of conduit for physical protection, it doesn't have to be a complete assembly. That if the only reason you're running conduit is for physical protection, you only have to run conduit where it needs protection, not all the way back to both boxes.
The exception is there, because otherwise 300.18 would contradict 300.15 (C), 334.15 (B), and so on.
from:
http://www.co.henrico.va.us/dyn/med_...00/318/NEC.pdf.
As for your weird little notion about "especially with PVC" (here and at Holt's)... ever wonder what PVC cement might do to the wire insulation?