Steve.Peel
Member
The AHJ has required me to isolate my uninsulated equipment grounding conductor (bare aluminum ground in SER AL cable) from contact with bare copper grounds from NM cable where they could or do come in contact before being lugged at the ground bar. Upon request for code references, the following were provided:
Code Ref: 110.14 - 250.70 - 342.14 - 344.14 etc. etc.
Galvanic action (NEC 342.14 and NEC 344.14) being the main reason for the requirement.
Can anyone shed some light on this for me? I believe that the potential for galvanic action (if there is any) rests in the fact that the two dissimilar metals are bonded together (as required) at the ground bar. Can contact between wire of differing metals outside of termination points cause or increase likelihood of galvanic action?
Code Ref: 110.14 - 250.70 - 342.14 - 344.14 etc. etc.
Galvanic action (NEC 342.14 and NEC 344.14) being the main reason for the requirement.
Can anyone shed some light on this for me? I believe that the potential for galvanic action (if there is any) rests in the fact that the two dissimilar metals are bonded together (as required) at the ground bar. Can contact between wire of differing metals outside of termination points cause or increase likelihood of galvanic action?