I need your help. I have not sized the Neutral, Main Bonding Jumper, or the Grounding electrode conductor in a while. Please check my work. Im feeling unsure. Ive been out of school for quite a few years now. Thanks for your help.
Transformer:
75KVA
Primary-480v 3Ph 3w - (3#1 & 1#6G)
Secondary- 120/208V 3Ph 4w - ( 4#4/0 & 1#2G)
Neutral: Art.250.66 Table
Largest Ungrounded Conductor - #4/0 Cu Conductor
Neutral Size: #2 Cu Conductor
(This seems too small to me.)
Main Bonding Jumper: #2 Cu
(Uses same table and math as the Neutral)
( This seems too big to me. Arent most Y transformers bonded when made with that metal strap that connects to the frame from the coils?)
Grounding Electrode Conductor:
This one has me a little puzzled.....250.66 Table says to use #2 copper. Article 250.66(A) says you only have to use #6 copper for the connection to the rod. So would you install #2 and bug a #6 to attach to the rod? Or could you use #6 for he entire run? Thanks!
Transformer:
75KVA
Primary-480v 3Ph 3w - (3#1 & 1#6G)
Secondary- 120/208V 3Ph 4w - ( 4#4/0 & 1#2G)
Neutral: Art.250.66 Table
Largest Ungrounded Conductor - #4/0 Cu Conductor
Neutral Size: #2 Cu Conductor
(This seems too small to me.)
Main Bonding Jumper: #2 Cu
(Uses same table and math as the Neutral)
( This seems too big to me. Arent most Y transformers bonded when made with that metal strap that connects to the frame from the coils?)
Grounding Electrode Conductor:
This one has me a little puzzled.....250.66 Table says to use #2 copper. Article 250.66(A) says you only have to use #6 copper for the connection to the rod. So would you install #2 and bug a #6 to attach to the rod? Or could you use #6 for he entire run? Thanks!