What is the reasoning behind not allowing different kinds of cables like this in the same duct or cable tray?
Both are insulated well enough to contain their respective voltages. What is the hazard of having them lying among each other?
plus I see enclosures with a couple runs of panduit inside. Is something that a sufficient barrier? What constitutes a sufficient barrier?
Its the same reason why conductors for power and lighting can't not be in the same enclosure. box or raceway with limited energy/signaling conductor (but what about unless insulated for the same voltage-thats not what the NEC says)
Enclosures with wiring duct inside may be mfg under UL508A, which by the way does not allow a Cat 5e with power wiring, although its done all the time.
Oh sorry the hazard is if the insulation is damaged, the low voltage/limited energy equipment can be damaged by overvoltage.
Huh? If the insulation is damaged, most anything around could be damaged.
In this day and age where everything has to communicate with each other, it just seems like an unnecessary restriction without any good reason that I can see.
Its the same reason why conductors for power and lighting can't not be in the same enclosure. box or raceway with limited energy/signaling conductor (but what about unless insulated for the same voltage-thats not what the NEC says)
Article 800 is for telecommunications and I am not sure if Cat 5e falls into that article, it was 725 but something tells me it may of changed.
Huh? If the insulation is damaged, most anything around could be damaged.
In this day and age where everything has to communicate with each other, it just seems like an unnecessary restriction without any good reason that I can see.
Huh? If the insulation is damaged, most anything around could be damaged.
In this day and age where everything has to communicate with each other, it just seems like an unnecessary restriction without any good reason that I can see.