Service Mast
RooKie12
SE no because it isn't rated for wet locations like USE is. A mast on the side of a building inside the pipe is considered a wet location under the 2008NEC
300.9 Raceways in Wet Locations Above Grade. Where
raceways are installed in wet locations abovegrade, the interior
of these raceways shall be considered to be a wet
location.
Insulated conductors and cables installed in raceways
in wet locations abovegrade shall comply with
310.8
310.8(C) Wet Locations. Insulated conductors and cables used
in wet locations shall comply with one of the following:
(1) Be moisture-impervious metal-sheathed
(2) Be types MTW, RHW, RHW-2, TW, THW, THW-2,
THHW, THWN, THWN-2, XHHW, XHHW-2, ZW
(3) Be of a type listed for use in wet locations
electricmanscott
Boston, MA
location.
310.8
You have proven your own point wrong.
SE cable has RHW RHW-2 XHHW XHHW- conductors
It is also not prohibited from being used in wet locations (this should be obvious consdiring what the cable is manufactured for)
Not in wet location
See above
macmikeman
Also SE cable is sunlight resistant as well. On Alcan SE cable the outer sheath is clearly marked with "sunlight resistant" and it has XHHW label markings for the conductors.
