tie wraps in a health facility

Status
Not open for further replies.

steve holt

Member
Location
Hawaii
Are there any restrictions on using tie wraps in a health facility? The I am using hospital grade MC and plenum rated LV comm wire. The ceilings we are running in are not plenum spaces. I have been told that the tie wraps need to be fire rated.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
What are you "tie wrapping" to?

Generally, low voltage cables and MC cables would need their own support. Tie wrapping to existing piping or conduits would not be allowed.

Steve
 

nyhockey

Senior Member
Location
long island, ny
About 15 years ago during a final inspection in NJ, I was told to remove all the ty wraps in the panels (5). The inspector realising I was a young out of state contractor that would have done just about anything to get the final, told me he did not like them becaues if one wire got hot they all would.
 
About 15 years ago during a final inspection in NJ, I was told to remove all the ty wraps in the panels (5). The inspector realising I was a young out of state contractor that would have done just about anything to get the final, told me he did not like them becaues if one wire got hot they all would.



Who says you were young 15 years ago?;):D

I know better....
 