Industrial Control Panel with:
Ground for a 480VAC, 3 phase, 30Amp power supply.
Ground for a 480VAC to 120VAC 100VA Control Transformer.
Ground for a 120VAC to 24VDC 15W power supply (this power supply operates a 4-20mA signal loop). This ground is for the 120VAC primary side of the 120VAC to 24VDC 15W power supply.
We have a 120VAC PID Temperature Controller. It has no ground connection. The PID Temperature Controller has a 2-wire, 4-20mA output. We have a (2-wire with shield cable) connected to the 24VDC power supply and a temperature transmitter/thermocouple assembly.
A request has been made to ground the shield on the 4-20mA PID output. We know that the shield should only be grounded at one end. We cannot ground it to the PID controller because it has no ground. The request is that we ground the shield to the same ground used for the 480V, 3-phase, 30Amp power supply, the 480VAC to 120VAC 100VA control transformer and the 120VAC to 24VDC power supply.
Should'nt the shield wire for the 4-20mA signal loop have a separate isolated ground?
Ground for a 480VAC, 3 phase, 30Amp power supply.
Ground for a 480VAC to 120VAC 100VA Control Transformer.
Ground for a 120VAC to 24VDC 15W power supply (this power supply operates a 4-20mA signal loop). This ground is for the 120VAC primary side of the 120VAC to 24VDC 15W power supply.
We have a 120VAC PID Temperature Controller. It has no ground connection. The PID Temperature Controller has a 2-wire, 4-20mA output. We have a (2-wire with shield cable) connected to the 24VDC power supply and a temperature transmitter/thermocouple assembly.
A request has been made to ground the shield on the 4-20mA PID output. We know that the shield should only be grounded at one end. We cannot ground it to the PID controller because it has no ground. The request is that we ground the shield to the same ground used for the 480V, 3-phase, 30Amp power supply, the 480VAC to 120VAC 100VA control transformer and the 120VAC to 24VDC power supply.
Should'nt the shield wire for the 4-20mA signal loop have a separate isolated ground?