mshields
Senior Member
- Location
- Boston, MA
In a high rise, can a life safety panel on say the 5th floor, feed loads on say the 9th floor? i.e. is there a requirement for how far away the source can be?
In a high rise, can a life safety panel on say the 5th floor, feed loads on say the 9th floor? i.e. is there a requirement for how far away the source can be?
on a similar subject
700.9 states emergency circuits shall be independent of all other wiring.(no emergency and normal in the same conduit) but it list 4 exceptions , other than the transfer switch can anyone help clarify the other 3 examples
[/COLOR][/SIZE]
One of the examples would be a unit type fixture, such as a 2-lamp emergency wall pack. Another would be the junction box that has the wiring supplying such a fixture as mentioned in my first sentence.
But I gather what I'm hearing is, that this is neverthelss NOT a code violation. True?
Interesting input Charlie on the terms emergency vs life safety. So I gather you only use the term life safety in a hospital situation to differentiate between the two types of emergency power that exists for a hospital. For a non-hospital since there is no division of the emergency system, it is appropriately referred to as the emergency system. Correct?
The "essential electrical system," including the life safety branch, the critical branch, and the equipment system, all come under article 700. Reference: 517.26.I think the life safety circuits in a hospital are covered by NEC 701 (legally required standby) if I remember correctly. An emergency system may be used in addition per article 700 (Emergency).
Quite correct.So I gather you only use the term life safety in a hospital situation to differentiate between the two types of emergency power that exists for a hospital. For a non-hospital since there is no division of the emergency system, it is appropriately referred to as the emergency system. Correct?
[/COLOR][/SIZE]
One of the examples would be a unit type fixture, such as a 2-lamp emergency wall pack. Another would be the junction box that has the wiring supplying such a fixture as mentioned in my first sentence.