Kartracer087
- Milwaukee WI
Here is the proposed system, and I want to know if this is the correct way to ground it:
A 480V 3 phase 3 wire bus feeds a 100kva transformer. The secondary is 208Y/120 3ph 4w. The secondary lines are connected to a circuit breaker which is a disconnect for a meter stack. The meter stack provides power to condo units at 208/120 single phase, the disconnects for each unit are in the meter stacks, so the tenant panels are main lug only. If this was the case, then would you run your 2 phase wires, a neutral, and a ground wire back to the meter box and have the tenant panels have isolated grounding busses (not connected to the neutral). So this would mean that the required bonding connection would be made at the meter stack, one bond connection to neutral for each tenant unit. If I'm seeing this right, then the main feeders from the transformer to the meter stack would simply be the 3 phase wires and a neutral. No bonding connection between the neutral and ground would be made at the transformer, only at the meter stack. Do I have the right idea here?
