normbac

Senior Member
On a heat pump do you add 1.25 to the minimum circuit amps that the manufactures plate states, or is that already factored in to the MCA
TIA
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You may size your conductor using the MCA number (no multiplier)
 

DARUSA

Senior Member
Location
New York City
On a heat pump do you add 1.25 to the minimum circuit amps that the manufactures plate states, or is that already factored in to the MCA
TIA
Size your conductor based MCA (Minimum Circuit Ampacity) and size your OPD base on the MCB (Maximum Circuit Breaker) or MFS (Maximum Fuse Size)required by the nameplate!
 