I am having a hard time wrapping my head around part of 225.32. The reason being is a discussion I had/am having about a generator install.
The discussion is about the gen. set disconnect. My point of view is the breaker on the gen.set doesn't meet 445.18 or 225.36 and I think that there is a large group here that concur. That said 225.32 says that the disconnect can be located inside or outside the building or structure it serves. But it also goes on to say it shall be in a readily accessible location nearest the point of entry. The nearest point of entry is what I am scratching my head about. I know what 230.70 A 1 states as to service conductors and I agree with having the least amount of unprotected conductors entering the building. But 225 covers branch circ. and feeders. I cannot see the point of having the "nearest point of entry" wording for the feeders. The feeders are protected by the OCP on the gen.set even though it may not be considered the disconnecting means the feeder conductors are still protected.
Here is a set up to illustrate what I am speaking of.
If you were to mount a SE rated ATS it would need to be located at the closest point of entry to the service conductors to comply with 230.70 A 1. Then you brought in the feeders from the gen set and because of location your run was 20 ft inside the building. By the wording of 225.32 you could be failed on the install. The only course would be to add another disconnect at the point of entry of the feeders which would be redundant. Dose this make sense or has the pain killers for my back kicked in yet?
The discussion is about the gen. set disconnect. My point of view is the breaker on the gen.set doesn't meet 445.18 or 225.36 and I think that there is a large group here that concur. That said 225.32 says that the disconnect can be located inside or outside the building or structure it serves. But it also goes on to say it shall be in a readily accessible location nearest the point of entry. The nearest point of entry is what I am scratching my head about. I know what 230.70 A 1 states as to service conductors and I agree with having the least amount of unprotected conductors entering the building. But 225 covers branch circ. and feeders. I cannot see the point of having the "nearest point of entry" wording for the feeders. The feeders are protected by the OCP on the gen.set even though it may not be considered the disconnecting means the feeder conductors are still protected.
Here is a set up to illustrate what I am speaking of.
If you were to mount a SE rated ATS it would need to be located at the closest point of entry to the service conductors to comply with 230.70 A 1. Then you brought in the feeders from the gen set and because of location your run was 20 ft inside the building. By the wording of 225.32 you could be failed on the install. The only course would be to add another disconnect at the point of entry of the feeders which would be redundant. Dose this make sense or has the pain killers for my back kicked in yet?