Bob - k = 12.9 ohm would be for the 75c rating. So even though I'm looking at max running amps being 140A, I still need to size the wire according to it being 200A since it is connected to a 200A CB right? Using that calculator sets me back at the original 600kcmil so I would have to buy a 750kcmil unless I look at parellelling since okonite doesn't carry a 600kcmil.
Rick - The service company is upgrading an existing 200A panel to 400A to accomadate for the new trailer being installed 780ft away from the panel. So we will have to look at cost for a disconnect < 30ft away I'm guessing.