I went on an emergency call today. H O was getting jolted when taking a shower and touching cold/hot handles. I took a reading between drain and handles( with water in tub ) and got 25V. Went outside to water main entrance and found new UG pvc water pipe to new well, where 1" steel piping used to be) Well not to my surprise, the rest of the steel water piping for the house was not bonded to GEC. Bonded the pipe and no longer had the 25V reading. I also searched round the attic and found 3 homeruns running most the lenth of the cold and hot steel pipes, within 1/2" or so. Would this be a case of induced voltage with no place to go? I found numerous loose connections on the neutral bus, tightened all neutral connections at panel. The panel is FPE originally installed in '68 with original ungrounded romex. She had a previous electrician install devices/circuitry around 8 weeks ago and I found his work to be sub-par...eventually he tied it in to existing ungrounded circuitry. At one switch location in house I read 30 volts between ground and neutral. I suggested that we disassemble the wiring starting with the most previous work first, since she earlier told me that the shower shock had been progressivly getting worse. Any words on what might be going on here?