I have a run of 5 light poles.
120 volts, 100watt fixtures, 500' long, 200' to first pole, 15 foot tall poles.
The spec is #10 AWG Cu., 20 amp circuit.
Is it an incorrect by code standards to run #10 to first and second light pole, and then #12 for the remaining 3 fixtures.
This would be at 3% voltage drop.
As the load decreases but the length increases is it incorrect to down size the wire.
Now this is spec. at #10, that is what will be installed, this is more a question in my mind and am I applying voltage drop with wire size correctly.
Also, it would be more trouble than what it is worth to set up different size wire for such a short length