Lightinghit88
Member
Where in 2008 code does it reference the amount of service cable that can enter a res.?
This is as close as you will get.Where in 2008 code does it reference the amount of service cable that can enter a res.?
230.70 General.
Means shall be provided to disconnect all conductors in a building or other structure from the service-entrance conductors.
(A) Location. The service disconnecting means shall be installed in accordance with 230.70(A)(1), (A)(2), and (A)(3).
(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
I have always understood it was 3 feet but have heard of max 5 feet.
not in the NEC, set by your local codes....Here it's 5 ft.
This is as close as you will get.