Service Entrance Conductor Marking

Status
Not open for further replies.

czars

Czars
Location
West Melbourne, FL
Occupation
Florida Certified Electrical Contractor
For years here in Florida we have stripped the outer sheath off the 4 conductor service entrance cable and used the three insulated conductors for the service entrance conductors down the service mast even though the conductors themselves are not marked. Is this no longer an acceptable practice?
 

jwjrw

Senior Member
I dont see anything in 230 that says they have to be marked. Not sure where else to look.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
For years here in Florida we have stripped the outer sheath off the 4 conductor service entrance cable and used the three insulated conductors for the service entrance conductors down the service mast even though the conductors themselves are not marked. Is this no longer an acceptable practice?
It hasn't been legal for many years but if you left it in the jacket you would be fine. Now, why do you install se cable inside conduit? It is a waste of money.
 