Sorry, Gus, but I don't understand that. If we are talking about a service or a main power feeder, then the discussion of interior feeders in 338.10(B)(4) does not apply. If we are not, then 310.15(B)(6) would not apply.
In addition, the connection between "derating" and 338.10(B)(4) is that you are led to 334, and specifically to 334.80, and the discussion of derating there is all about multiple current carrying conductors in the same raceway. As I said earlier, that would not apply to this installation.
Finally, you can't use the word "derating" in the context of table 310.15(B)(6). You don't have an ampacity value to start with, so you can't get a derated ampacity value to end up with.
So what would you be looking for, what is the reason for rejecting this install, and what would the electrician have to change, in order to pass inspection?