AC roof-top unit as a raceway

Status
Not open for further replies.

smallfish

Senior Member
Location
Detroit
Feeder conductors with an equipment grounding conductor are piped into the bottom of a roof-top AC unit. Once inside the roof-top AC unit, these insulated conductors are not run in any raceway but are bundled together and pass three feet through the unit through a bushed hole into a diconnnect switch mounted on the outside. The conductors return thru a bushed hole back into the AC unit and are then wire-nutted to short conductor leads extending from a bushed hole in the controller enclosure. (Apparently the factory-installed leads were meant to be wirenutted outside its control enclosure, but inside the AC unit.) It looks wrong, but is it correct to run un-enclosed feeder conductors inside an AC unit and is it correct to wire nut the conductors to the factory leads without this termination being enclosed in some kind of box enclosure? The wires do not appear to be subject to abuse.
Thanks
 

donselectric

Senior Member
Location
nh
would it have made that much of a diff if you came up the side to the disco??
i wouldnt let that go neither...its not fac so i want protection....
 

jusme123

Senior Member
Location
NY
Occupation
JW
the whole point of the disconnect is to deenergize all open wiring(unprotected conductors) and components within the enclosure. When the disconect is in the 'off' position, there should be minimal risk within the enclosure of being injured. With unprotected conductors with 480V live in a unit with the disconnct in the 'off' position, hardly offers a minimal risk of injury.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
the whole point of the disconnect is to deenergize all open wiring(unprotected conductors) and components within the enclosure. When the disconect is in the 'off' position, there should be minimal risk within the enclosure of being injured. With unprotected conductors with 480V live in a unit with the disconnct in the 'off' position, hardly offers a minimal risk of injury.
all well and good. now, put on an inspector's hat and reject it noting a Code reference :)
 

jwjrw

Senior Member
the whole point of the disconnect is to deenergize all open wiring(unprotected conductors) and components within the enclosure. When the disconect is in the 'off' position, there should be minimal risk within the enclosure of being injured. With unprotected conductors with 480V live in a unit with the disconnct in the 'off' position, hardly offers a minimal risk of injury.

But the disconnect and the enclosure are two different things. I thought I read it went thru unit to disconnect on side,back inside unit. You only remove power from the load in a disconnect.
 