I am in PA and assume the permit was pulled before Jan 1 so the 2005 NEC applies. The main difference is that "all loads" is not in 2005 which is the one that would apply in this particular case.
My humble opinion as an inspector:
1) 310.15(B)(6) would apply due to the language in NEC 2005
2) The neutral must be the larger of the 2: Calculated load or 250.122
3) I would want a calculated load for the service too (garage and house)
Outside of the inspector hat:
1) I would not want to find or pay for a 200A breaker to feed the house from the other panel (bolt on maybe but then not pay for it)
2) Disco outside the garage with double lugs to feed both the garage and house as mains or properly rated meter base with double lugs.
My humble opinion as an inspector:
1) 310.15(B)(6) would apply due to the language in NEC 2005
2) The neutral must be the larger of the 2: Calculated load or 250.122
3) I would want a calculated load for the service too (garage and house)
Outside of the inspector hat:
1) I would not want to find or pay for a 200A breaker to feed the house from the other panel (bolt on maybe but then not pay for it)
2) Disco outside the garage with double lugs to feed both the garage and house as mains or properly rated meter base with double lugs.