Does anyone know where the code refernece is requiring a disconnect when the service entrance cable is further than 10 foot from the metercan to the panel? Thanks.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Does anyone know where the code refernece is requiring a disconnect when the service entrance cable is further than 10 foot from the metercan to the panel? Thanks.
The distance may be a local requirement but it is not an NEC requirement.
Look at art. 230.70(A)(1)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Around here 10' into the building and you'll get a red violation sticker which means you'll either move the panel closer or put the OCPD adjacent to the meter.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I see 230.91

That section deals with the service overcurrent protective device, which usually will be intragral with the service disconnecting means.

230.70(A)(1) is the requirement for the service disconnecting means to be located nearest the point of entrance on the service conductors.

Chris
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Around here 10' into the building and you'll get a red violation sticker which means you'll either move the panel closer or put the OCPD adjacent to the meter.
Remember, you can also place the main disco inside, back-to-back with the meter, and still have the panel elsewhere.

Of course, in most cases, you'd probably put the panel there if a main disconnect could go there. I'm just sayin . . .
 

jwjrw

Senior Member
That is quite generous. In my area there is no "official" length that service conductors can run in side a building.

Chris

I looked this one up on our countys web under electrical interpretations
our chief elec inspector approved it
www.charmeck.org
Go to code enforcement and electrical then the interpertations.
 