MC-AP cable

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
You might have to use bonding bushings with MC-AP cables running above 250 volts to ground and entering concentric KOs.

See 250.97
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I'm with Bob, the voltage of the system may trigger the requirements of 250.97. For under 250 volts I wouldn't worry about it.
 