I'm working on a Credit Union with (6) VAT drive-up units. Each blower motor needs 9A @ 120V. The commercial drive-up has (2) motors, so there are (7) motors total.
I've guessed that only (2) of the motors will be on simultaneously for my load calc. In other words, I put (5) of the motors under non-coincidental or non-peak loads.
Is there anything in the NEC that covers this?
Similar to Table 220.54 for clothes dryers.
The reason is that it's a renovation job. The main 400A panel (A) has a 100A breaker feeding a 200A panel (B) that in-turn feeds (2) more panels (C&D). If I leave ALL the blowers at 100% demand, panel B calculates at 115A which is too much for the 100A feed.
I could reconfigure the one-line and feed panel C or D from panel A, instead of B, but why spend the money since the blowers are not likely simultaneous.
I've guessed that only (2) of the motors will be on simultaneously for my load calc. In other words, I put (5) of the motors under non-coincidental or non-peak loads.
Is there anything in the NEC that covers this?
Similar to Table 220.54 for clothes dryers.
The reason is that it's a renovation job. The main 400A panel (A) has a 100A breaker feeding a 200A panel (B) that in-turn feeds (2) more panels (C&D). If I leave ALL the blowers at 100% demand, panel B calculates at 115A which is too much for the 100A feed.
I could reconfigure the one-line and feed panel C or D from panel A, instead of B, but why spend the money since the blowers are not likely simultaneous.