Driven Ground Rod.

Status
Not open for further replies.

ARF

Member
Guys I am working on a parking lot project where the inspector has insisted that a driven ground rod be installed at each light pole. We have provided a ground wire to each pole from the panel but, I am now wondering that if we install these rods will we need to run an additional ground electrode conductor to the building ground point ? If so would this be required whenever a ground rod was installed:confused:
 

ARF

Member
Not an NEC requirement. It may be a job spec, however.
Thanks, that's what I thought but I was concerned that somehow NEC 250.50 could be interpreted to mean that if a rod(s) were installed they could be considered as part of 250.52(5).
 

RICK NAPIER

Senior Member
Location
New Jersey
See article 250.54 auxiliary grounding electrodes they used to be called supplementary electrodes but they got confused with supplemental electrodes. In short they don't have to bond back to the building or any where else.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Here's the 2005 version before the change in wording:

1100203707_2.jpg
 