mcclary's electrical

Senior Member
Location
VA
Working in a 60's era home yesterday. Splicing into an existing piece of 14/2 in the attic.I cut wire, stripped sheath, and there was a factory splice made in the white wire. It was stripped about 1/2",,,laid on top of each other, and crimped, (not welded). Then it had a piece of clear heat shrink over the crimp so the crimp was visible, And then the sheath over that. You could actually see the heat shrink on the inside had a dark spot from the crimp getting warm. I think this is poor practice, is it legal? Is all NM manufactured that way and I never was lucky (or unlucky)enough to find one?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I've never found a splice in a cable, but I did find a hand-knotted and NON-insulated joint in a roll of THWN/THNN several years ago.

We were wiring gas pumps. We might have missed it if I didn't have the habit of combing the wires with my fingers as they un-spool.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
chances are if you stay in the field you will eventually find another one or one that is "open". I've found two over four decades.
 

jwjrw

Senior Member
I have found welded butt splices in NM and mc cable

Wow I've never heard of it and I's swear its an old electricians tale if I hadnt heard it here. And I still want to see one before I totally believe it!:grin:
 

kbsparky

Senior Member
Location
Delmarva, USA
Found something similar on a job about 15 years ago:

We had roughed-in a new circuit for a wall heater in a bathroom. Went to trim it out a couple weeks later, and the heater would not work.

Troubleshooting revealed that we had power at the panel, but nothing at the heater. Single run of romex, no splices or junctions, etc.

Since there was an open ceiling in the basement below, we ran a new piece of romex, and fished it in ---> heater worked fine after that.

Removed the old piece of wire, and stripped it open to determine why it had no continuity from one end to the other, and viola! There was a jack-leg splice inside of the cable sheath, with a bad crimp on the grounds, and open gaps in both the black and white conductors! :confused: This gap was about several inches to a foot with no connection! :mad:

I took that piece of wire back to the supply house, and explained the time and trouble I went to over it, and suggested that the manufacturer might be held liable for such poor quality control, etc.

They gave me a 1000 foot spool as replacement for the bad piece of wire, since it was originally on that size reel. They generally don't reimburse for labor, but replacing the whole reel for a 25 foot piece was enough for me at the time. ;)
 

charlie k.

Senior Member
Location
Baltimore, Md.
Years ago I wired a house for a friend. He had a family room with cathedral ceilings. I picked up some 14/2 and started wiring the recessed lights. When I started the cable had hot, neutral and ground. After about 3 lights when I cut the cable it did not feel right. The ground disappeared. About 100' of the roll was missing the ground. Supplier did make good.

Charlie
 

mivey

Senior Member
I bet it is still made that way.
I would not think so since it doesn't seem very efficient given the modern equipment, but who knows.

The facility I have been in joins the ends with a butt-end arc weld. The splices I have found in the field (look for a knot in the cable) have also been joined with a butt-end arc weld.
 

c2500

Senior Member
Location
South Carolina
I had a roll of THHN #8 that 80' or so into the roll it looked pregnant. It was some kind of repair/defect. Supply house took it back. I would like to have known what was under the mess, but I had no cut any of the wire yet.

c2500
 

mivey

Senior Member
I had a roll of THHN #8 that 80' or so into the roll it looked pregnant. It was some kind of repair/defect. Supply house took it back. I would like to have known what was under the mess, but I had no cut any of the wire yet.

c2500
Those big knots set off an alarm on modern machines. They even measure the amount of insulation applied down to the thousanths of an inch on wire that is flying by at high speed. I suspect human error let it get by. When you are in a wire plant, there is a constant barrage of alarms that are being attended to by the workers. Sometimes the workers do the right thing, sometimes they don't.
 