Because it is a design issue and not a code issue.
Would green and white be considered design issues?
I think its a safety issue not having a standard color code for the two widely used systems in the USA (120/208v and 277/480v). Take a look at 90.1(A)
I don't believe it's because it's a design issue.
I honestly believe it's because it would cause other problems. For example, how many times have you seen red thhn that was really pink or orange. I've seen yellow that was orange, gray that looked black, etc etc etc.
It's hard enough for the manufacturers just to get green and white right.
White and green (as well as gray and green with one or more yellow stripes) are reserved respectively for the grounded and grounding conductors. Thier proper identification is a safety issue.
What if you opened a box and checked two different red wires to ground, wire 1 read 120v to ground, and wire 2 to ground read 277v. If the code was changed, the one red wire would have to be either brown/orange/yellow.
Every electrician has violated 200.6 and 250.119.
Then a qualified electrician [per 90.1(C)] would know it was installed prior to adoption of the 2008 NEC.
Now consider this: How would you treat a gray wire?
I don't remember you inspecting my work. How did you know? :grin:
Would green and white be considered design issues?
I think its a safety issue not having a standard color code for the two widely used systems in the USA (120/208v and 277/480v). Take a look at 90.1(A)
If all/most electricians use the standard black,red, blue for 120/208v and brown, orange, yellow for 277/480v, why does the NEC remain silent? :-?
Because even when the NEC is not silent it is often ignored.
None of us should trust a color to tell us anything.
What if you opened a box and checked two different red wires to ground, wire 1 read 120v to ground, and wire 2 to ground read 277v. If the code was changed, the one red wire would have to be either brown/orange/yellow.
This situation is covered by the NEC 210.5 (C) Ungrounded conductors, where more than one nominal voltage is present each branch circuit conductor where accessible shall be identified by system.
What would prevent me from identifing all my 120/208 ungrounded conductors as black and all my 277/480 ungrounded conductors as red?
What would prevent me from identifing all my 120/208 ungrounded conductors as black and all my 277/480 ungrounded conductors as red?