jetlag
Senior Member
- Location
- Eatonton, Georgia
I going to remove a double meter base on duplex apartment. Owner wants to go back with seperate service on each apart. The present service is 100 amp each side with no outside disc. Im going to add 100 amp outside disconnects and run 4 conductor wire to panels. My question is can I use 100 amp dissconnects with out a main breaker and install 100 breaker to supply the feeder or do I need a 100 amp main and come off the main lugs at bottom. The problem is the supply houses here only have main lug 100a disc but the 200 amp have main breaker. If I backfeed a 100 amp mounted on the buss to form a main then I would have to install another 100 a breaker to supply the feeder.