NEC 300.4(E) requires wiring that is not GRC of IRC to be installed 1 ? inch away from ?nearest surface? of roof decking. If I have a pan deck roof with a channel that is 4? wide and 3? deep I read the code as being able to install wiring in the ?Chase? of the pan deck as long as no part of the wiring is within 1 ?? of any surface of the pan deck. The picture in the Analysis of Changes to the 2008 NEC states and shows in pictures that the wiring must be installed 1 ?? from the lowest part of the pan deck. What is the proper interpretation?