Not too hot at the termination?

Status
Not open for further replies.

Dale Hayes

Senior Member
For 75C rated terminations, a higher temperature rated conductor can be used, but the ampacity of the conductor must be based as if the conductor is rated 75C.

What size 200C (SRML) wire is required in order to end up with 50Amps and keep the termination temperature at 75C?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I don't understand the question. What is "SMRL," and are you suggesting there exists a conductor with an insulation system rated for 200C? Also, are you talking about a situation that requires derating a conductor, such as the ambient temperature being over 30C, or having more than three current-carrying conductors in the same raceway?
 

Dale Hayes

Senior Member
SRML is a high temperature wire (aka as type SA). See NEC 310.18.
This scenario is no more than (3) conductors based a a 40C ambient.
 

jghrist

Senior Member
Assuming 0-2000V, 30?C ambient, and no more than 3 conductors in a raceway, you would need No. 8 copper to have 50A ampacity with a 75?C rating. It doesn't matter if the insulation is rated at 75?C or 200?C.
 