KELLY YOUNG

New member
I HAVE A BIDDING SOFTWARE. I BID A JOB WITH A 600 AMP SERVICE AND IT SHOWED TO DO IT IN 300 PARALLEL AND I DID NOT LOOK AND I SENT THE BID. LATER WHEN I WAS GOING BACK THROUGH MY NOTES, I NOTICED IT WAS IN 300'S. WHEN i LOOKED UP 300 & 75C, i NOTICED THAT IS ONLY GOOD FOR 285 AMPS. IS THIS BIDDING PROGRAM WRONG OR IS THERE A RULE WHEN USING PARALLEL, YOU CAN USE 90C?:-?:-?:-?
THANKS,
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Welcome to the Forum. The software is assuming a calculated load of 570A or less. 240.4(B) allows the use of a 600A OCPD.

Check your caps lock.:)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You cannot use the 90 degree C ampacity simply because these are parallel conductors. Chris gave you the answer when applying the next standard size rule in 240.4(B) so it may or may not work depending on your calculated load. Please turn off your CAPS lock. It makes your post harder to read and is construed as shouting.

Welcome to the Forum. :)
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Hopefully that is your only problem :) I didn't see in your OP if the parallel conductors are in 1 conduit or paralleled in 2 conduits.
De-rating will introduce another possible problem.
 