Here are the specs on the heater, then my questions will come:
Here is a link to the heater: http://www.cpotanklesswaterheaters.com/powerstar/ae115_spec.html
Voltage: 240/208
Watts: 17.25/13kW
Amps: 2x40A (80A)
We currently have a 120/208Y XFMR rated at 45kVA. I want to add the water heater to the XFMR, but I want to make sure my thoughts are right as I have never done this before (I'm an EE right out of college).
I'll need two 40A breakers, so then I should feed these from two seperate phases so to calculate the kVA on each phase:
208 x 40/1000 = 8.32kVA
So if I have two breakers each at 8.32kVA, my total load on my XFMR will be 8.32 + 8.32 = 16.64kVA, is that correct?
I assume this will create a horrible imbalance unless I have other loads to make up for it on the 3rd phase. Would it be smarter to purchase a single phase XFMR for the heater?
Let me know if anything I said is incorrect.
Thanks.
Here is a link to the heater: http://www.cpotanklesswaterheaters.com/powerstar/ae115_spec.html
Voltage: 240/208
Watts: 17.25/13kW
Amps: 2x40A (80A)
We currently have a 120/208Y XFMR rated at 45kVA. I want to add the water heater to the XFMR, but I want to make sure my thoughts are right as I have never done this before (I'm an EE right out of college).
I'll need two 40A breakers, so then I should feed these from two seperate phases so to calculate the kVA on each phase:
208 x 40/1000 = 8.32kVA
So if I have two breakers each at 8.32kVA, my total load on my XFMR will be 8.32 + 8.32 = 16.64kVA, is that correct?
I assume this will create a horrible imbalance unless I have other loads to make up for it on the 3rd phase. Would it be smarter to purchase a single phase XFMR for the heater?
Let me know if anything I said is incorrect.
Thanks.