Q: Dividing BTUH by 3413 gives to KW. Is this mechanical or electrical KW? I mean is this the electrical KW the machine will consume?
 

akhan_08

Member
Location
Pakistan
KW or Btu/h?

KW or Btu/h?

This is cooling capacity of the HVAC equipment not electrical load. This is S.I unit for Cooling capacity just as FPS unit which is BTulh.

The same unit is used in calculating electrical load KW i.e. we usually not use BTu/h for electrical loads as we don't have to remove heat from any space but we have to supply power to the equipment. Although electrical loads cause heating effect too but this effect is not significant here. So we use KW unit for Electrical load.
 
This is cooling capacity of the HVAC equipment not electrical load. This is S.I unit for Cooling capacity just as FPS unit which is BTulh.

The same unit is used in calculating electrical load KW i.e. we usually not use BTu/h for electrical loads as we don't have to remove heat from any space but we have to supply power to the equipment. Although electrical loads cause heating effect too but this effect is not significant here. So we use KW unit for Electrical load.

Thanks. Thats fine. Actually what we are looking for is the electrical power consumption required for the given BTUH of a HVAC unit where we dont have any other data sheet available. There must be some relationship between the two.
 

shamsdebout

Senior Member
Location
Macon,GA
Q: Dividing BTUH by 3413 gives to KW. Is this mechanical or electrical KW? I mean is this the electrical KW the machine will consume?

I found this excerpt from the IEEE Gray Book, I hope it helps.
With a known heat loss, the electrical load in kW can be obtained by dividing the estimated heat loss (Btu/hour) by
3413 since there are 3413 Btu in 1. kWh of electricity. Usually, it is necessary to use a demand factor of 100% for
electrical heating loads.
 

Hameedulla-Ekhlas

Senior Member
Location
AFG
I had faced same problem like you but I found a solution for this. It is night here 2moro in the morning I will go Office I have the solution I will inform you.
 

skeshesh

Senior Member
Location
Los Angeles, Ca
Shamsdebout's method is what I've also used in the past. Having said that it is not exactly accurate, especially with packaged heating products that are popular nowadays because other factors than a simple conversion between electrical rating to mechanical output effect the BTU/hr rating. But I guess if you have no other way of approaching this you got no choice right?
By the way, can you provide a bit more detail about what kinda unit this is? is it just a small standalone or does it serve a building, etc.
 

bob

Senior Member
Location
Alabama
A electric nickel chrome heater element produces 3.4 BTU/Hour
The very efficient mechanical refrigeration compressor produces 8.533 BTU/Hour+/-
I had a 4 ton unit 10 SEER that pulled 28 amps. That's 28x240 = 6720 kva /4ton = 1.7 kva per ton
One ton of frig.=12000 BTU/hour
1 watt=8.533 BTU/hour compressor

4 tons x 12,000=48,000 BTU/hour

48,000/8.533=5,625 watts 1.4 kw per ton 1.75 kva per ton

5,625 w/240 volts=23 amps more efficient machine

If you include the SEER, then you can do it another way. SEER is defined as the heat transferred per unit of energy, that is in BTU/watthour.

P = AC load/SEER

For your 4 ton unit and SEER = 10,

P = (48,000 BTU/hour)/(10 BTU/watthour) = 4,800 watts,

then throwing in PF,

I = P/(VxPF) = 4800W/(240V x 0.8) = 25A 1.2 kw per ton or 1.5 kva per ton

This is comparable to the other result.
 
A electric nickel chrome heater element produces 3.4 BTU/Hour
The very efficient mechanical refrigeration compressor produces 8.533 BTU/Hour+/-
I had a 4 ton unit 10 SEER that pulled 28 amps. That's 28x240 = 6720 kva /4ton = 1.7 kva per ton
One ton of frig.=12000 BTU/hour
1 watt=8.533 BTU/hour compressor

4 tons x 12,000=48,000 BTU/hour

48,000/8.533=5,625 watts 1.4 kw per ton 1.75 kva per ton

5,625 w/240 volts=23 amps more efficient machine

If you include the SEER, then you can do it another way. SEER is defined as the heat transferred per unit of energy, that is in BTU/watthour.

P = AC load/SEER

For your 4 ton unit and SEER = 10,

P = (48,000 BTU/hour)/(10 BTU/watthour) = 4,800 watts,

then throwing in PF,

I = P/(VxPF) = 4800W/(240V x 0.8) = 25A 1.2 kw per ton or 1.5 kva per ton

This is comparable to the other result.


Thanks Bob. Excellent calculation. But I just want to know what do we conclude from this? I mean what is the relation between a HVAC unit(BTUH) and the electrical power it consumes? Or, in other words, if we know the BTUH of an HVAC unit, what would be the input elect. power consumption?thanks
 

dereckbc

Moderator
Staff member
Location
Plano, TX
This might help for a bid estimate. To determine the load use this formula:

BTU / SEER = Watts. So if you have 4 tons of cooling and a SEER rating of 10 = 48,000 / 10 = 4.8 Kw.

But for the actual design use the manufacture spec sheet.
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Thanks Bob. Excellent calculation. But I just want to know what do we conclude from this? I mean what is the relation between a HVAC unit(BTUH) and the electrical power it consumes? Or, in other words, if we know the BTUH of an HVAC unit, what would be the input elect. power consumption?thanks
Sorry did not see this post. Consumption is hard to define because you would have to know the insulation factor, area of the room(s), temp differential. But as a ball park figure use 33.33% duty cycle in a 24 hour period or 8 hours. So 4.8 Kw x 8 Hours = 38.4 Kwh per day usage. To figure the load you would need the PF so if it was say .8 then 4.8 KW / .8 = 6 KVA.
 

bob

Senior Member
Location
Alabama
Thanks Bob. Excellent calculation. But I just want to know what do we conclude from this? I mean what is the relation between a HVAC unit(BTUH) and the electrical power it consumes? Or, in other words, if we know the BTUH of an HVAC unit, what would be the input elect. power consumption?thanks

Actually it is correct that one ton of air-conditioning is equal to 12,000 btu/hr. However the other question trying to convert a one ton A/C unit into kw/hr consumed is very dependant on the make and model of the air-conditioner, as well as its EER (energy Efficiency Rate). These range from 6-14 EER. Standard average one ton A/C unit consumes about 1.4 KW/hr.

Check http://www.engineeringtoolbox.com/cop-eer-d_409.h
 
A electric nickel chrome heater element produces 3.4 BTU/Hour
The very efficient mechanical refrigeration compressor produces 8.533 BTU/Hour+/-
I had a 4 ton unit 10 SEER that pulled 28 amps. That's 28x240 = 6720 kva /4ton = 1.7 kva per ton
One ton of frig.=12000 BTU/hour
1 watt=8.533 BTU/hour compressor

4 tons x 12,000=48,000 BTU/hour

48,000/8.533=5,625 watts 1.4 kw per ton 1.75 kva per ton

5,625 w/240 volts=23 amps more efficient machine

If you include the SEER, then you can do it another way. SEER is defined as the heat transferred per unit of energy, that is in BTU/watthour.

P = AC load/SEER

For your 4 ton unit and SEER = 10,

P = (48,000 BTU/hour)/(10 BTU/watthour) = 4,800 watts,

then throwing in PF,

I = P/(VxPF) = 4800W/(240V x 0.8) = 25A 1.2 kw per ton or 1.5 kva per ton

This is comparable to the other result.

Thanks Bob. Excellent calculation. So what do we conclide from this? What we are looking for is that if we know BTUH of an HVAC unit, what will be its power consumption, if we dont know SEER or we dont have any data sheet. In other words, converting BTUH value to KW(BTUH/3413) gives us mechanical KW and not electrical KW. If it is right, what would be electrical input KW?
Thanks.
 
Thanks Bob. Excellent calculation. So what do we conclude from this? I mean if we know BTUH of a HVAC unit but we dont know SEER, then how to find the electrical power consumption. In other words, converting BTUH to KW(BTUH/3413) will provide only mechanical KW but not electrical KW. Is that right? So what will be the electrical KW? Any relation?

thanks
 

kwired

Electron manager
Location
NE Nebraska
if you are trying to do a service or feeder load calculation I would assume a low SEER to make sure I allow enough capacity. Not sure if there are any new units being made anymore with a SEER below 12 or 13 pretty sure there are none below 10. If not a new unit sorry better figure for higher VA.
 
Thanks KWIRED. Agree to use lower SEER to get higher VA. Now, is EER is the same SEER?And one said EER will be from 6-14 . While other say SEER is never below 10. What is correct?
 

kwired

Electron manager
Location
NE Nebraska
according to this link since 2006 all new units needed to be 13 SEER or higher. I believe SEER is for seasonal energy efficiency rating and will not work directly for an electric load calculation. I know that most if not all of the higher SEER units will use a multistage compressor which means if the required demand is low they will use less energy by switching a valve to regulate refrigerant flow at a different rate, this will then put less load on the compressor. So for a maximum load you will need to know what the unit uses at the max demand stage which is probably EER. A good HVAC guy is probably a lot of help here, the guys that just do installs are usually not very sharp on sizing of units and other calculations.
 