Topic basically says it all, I have a job where the Project manager submitted a single phase panel as a sub panel from an existing 3 phase panel.
1) My argument is that supplying a single phase sub panel from a 3 phase Y regardless of the immediate load can potentially be used to severely unbalance the load at some point down the road.
2) Also as far as I know there is no panel board rated as 120/208v Y 3wire, only 4 wire.
Aside from the NEC requiring all equipment be rated and listed for the purpose I cannot think of anything else to possibly tell him. He also believes this sub panel which is in the very next room requires a main breaker, I see 408.36 allowing me to use the OCPD at the main panel board as my only disconnecting means.
Any information is appreciated.
1) My argument is that supplying a single phase sub panel from a 3 phase Y regardless of the immediate load can potentially be used to severely unbalance the load at some point down the road.
2) Also as far as I know there is no panel board rated as 120/208v Y 3wire, only 4 wire.
Aside from the NEC requiring all equipment be rated and listed for the purpose I cannot think of anything else to possibly tell him. He also believes this sub panel which is in the very next room requires a main breaker, I see 408.36 allowing me to use the OCPD at the main panel board as my only disconnecting means.
Any information is appreciated.