No specified depth. If there are comustibles, you need them. That begins with the guess that the Building Code sent you to NFPA 72 to determine installation requirements.
 
No specified depth. If there are comustibles, you need them. That begins with the guess that the Building Code sent you to NFPA 72 to determine installation requirements.

Thanks Ron. However I could not understand your second line of the paragraph. Could you please explain again.

thanks
gk
 

ron

Senior Member
The requirement for coverage areas are found in the adopted building code.
If it was up to 72 only, they would want it everywhere, but you don't need that in most installations.
 
The requirement for coverage areas are found in the adopted building code.
If it was up to 72 only, they would want it everywhere, but you don't need that in most installations.

Thanks Ron. By the way, th BS(British std) has specified it to be more than 800mm void above ceiling to have smoke detectors.
 