Basically if one were to use a 3ph 45kva transformer w, 480d-208y/120 as an example the primary of HV FLA would be 54.2 and the secondary 208 LV FLA would be 125.
If you were to apply an OCPD of either applied at 125% or the next standard rating of course the LV amperes is greater. One would expect that the inrush of magnetizing current would be the same percentage if the transformer was to be energized from either the HV or LV side which is an incorrect assumption. Because the LV windings are next to the core of the transformer the inrush is a much higher percentage, of the FLA. How much higher? There are no standard values available unless and engineer does some calculations for you.
If the inrush were to be 10X at 54.2 when energizing the HV winding one would expect the inrush ti be about 540A. Then it would be logical to expect the inrush to be 1250A (125x10) if you were to use tat same transformer as a step up. This is a wrong assumption however. Because the LV windings are next to the core that 1250A could easily be 50% more or as high as 1875A.
As such defining what the word "higher" means is important. The reason for the inrush is that the transformers? core goes into saturation until counter EMF can be established by the alternating current which last about 1/10 of a second before it settles down.
If a transformer has been designed for a step up application the LV windings are either placed on the outside of the HV windings or the flux desity is reduced. On 600v transormers the LV winding is normally place on the outside where the taps would be located. Please remember that it is very difficult to locat the taps in winding that are locatre in the inside.
On medium voltage transformers place the HV coils nest to the core is not a good idea. As such it is better to be left on the outside and the flux desity of the core reduced so that the core doesn't go into saturation as easily.
Basically there are no exact figures to go by and the objective is to know if you are playing in an area which can cause you grief. Use the highest rated OCPD as you are allowed by the NEC.
If you were to apply an OCPD of either applied at 125% or the next standard rating of course the LV amperes is greater. One would expect that the inrush of magnetizing current would be the same percentage if the transformer was to be energized from either the HV or LV side which is an incorrect assumption. Because the LV windings are next to the core of the transformer the inrush is a much higher percentage, of the FLA. How much higher? There are no standard values available unless and engineer does some calculations for you.
If the inrush were to be 10X at 54.2 when energizing the HV winding one would expect the inrush ti be about 540A. Then it would be logical to expect the inrush to be 1250A (125x10) if you were to use tat same transformer as a step up. This is a wrong assumption however. Because the LV windings are next to the core that 1250A could easily be 50% more or as high as 1875A.
As such defining what the word "higher" means is important. The reason for the inrush is that the transformers? core goes into saturation until counter EMF can be established by the alternating current which last about 1/10 of a second before it settles down.
If a transformer has been designed for a step up application the LV windings are either placed on the outside of the HV windings or the flux desity is reduced. On 600v transormers the LV winding is normally place on the outside where the taps would be located. Please remember that it is very difficult to locat the taps in winding that are locatre in the inside.
On medium voltage transformers place the HV coils nest to the core is not a good idea. As such it is better to be left on the outside and the flux desity of the core reduced so that the core doesn't go into saturation as easily.
Basically there are no exact figures to go by and the objective is to know if you are playing in an area which can cause you grief. Use the highest rated OCPD as you are allowed by the NEC.